Electric system
Many perks!
<...more...>


Sponsor
 

Google


Fauna Top Sites
Register Electric system Members Electric system Electric system Today's PostsElectric system Electric system Electric system
LOG IN/REGISTER TO CLOSE THIS ADVERTISEMENT
Go Back   Orchid Board - Most Complete Orchid Forum on the web ! > >
Reply
 
Thread Tools Rate Thread Display Modes
  #1  
Old 08-16-2022, 01:06 PM
Rothrock42 Rothrock42 is offline
Senior Member
 

Join Date: Dec 2015
Location: Portland, Oregon, USA
Posts: 283
Default Electric system

My new greenhouse is built in my backyard -- I hired somebody, I don't have construction skills. It is 15x11 feet. I also had water, natural gas, and electric services run to the side of the building.

But I'm trying to figure out what to do with the electrical.

I had an electrician setup a sub panel at the building. But since I'm not sure exactly what I'll need and where it should go, I was hoping to do some of the circuits on my own.

What I have:
  • At the main panel in the garage a 60 A breaker feeding the subpanel
  • A subpanel with an unusual breaker with a 40A shut off and two 20A breakers
  • One 20A breaker goes to one GFCI outlet inside and one 20A breaker is free.

What I want:
  • A circuit for my exhaust fan and ambient air intake
  • A circuit for my air circulation fans
  • A circuit for my misting system pump and maybe a wet wall pump.

Here are my questions and concerns:

The fans are all variable speed and some are controlled with a thermostat. Will that cause a problem with using GFCI outlets?

Also some of the plugs for fans are up high and if the GFCI outlets trip I'll have to get a ladder out. Would it be better to have AFCI/GFCI breakers?

If I go with AFCI/GFCI breakers will the variable speeds for the fans cause problems on those circuits.

Is a building shut off at the subpanel a good idea?

Does anybody have any resources? Or experiences they can share with AFCI/GFCI circuit breakers or outlets?

BTW: I know that I should have an electrician do this, but that will cost as much as the rest of the building and I can't afford that. And even if it ends up being to complicated have to find somebody I'll need to be able to explain exactly what I need.
Attached Thumbnails
Electric system-gh1-jpg   Electric system-services-jpg  
Reply With Quote
  #2  
Old 08-16-2022, 01:41 PM
rbarata rbarata is offline
Senior Member
 

Join Date: Mar 2015
Zone: 10a
Location: Abrantes
Posts: 5,522
Electric system Male
Default

Here, to build a gh like yours, you would need a permit. And to get it you would need to present a project covering not only the building but also all the systems (water, gas, electricity).
Even though, many times it is not allowed based on arquitecture or security. Needless to say that all the projects must be done and signed by a qualified engineer
Are you sure you can do it by yourself?
__________________
Meteo data at my city here.
Reply With Quote
Post Thanks / Like - 1 Likes
Likes Rothrock42 liked this post
  #3  
Old 08-16-2022, 02:34 PM
Ray's Avatar
Ray Ray is offline
Senior Member
 

Join Date: May 2005
Member of:AOS
Location: Oak Island NC
Posts: 15,149
Electric system Male
Default

GFCI's (GROUND Fault Circuit Interrupters) trip when the two "sides" of the alternating current curve become suddenly unequal, which is what happens if you, or part of the structure become a short to ground. Being a wet environment, all electrical equipment should be grounded.

They should not be affected in the least by variable-speed devices or those with automatic controls like thermostats, humidistats, or timers.

AFCI's (ARC Fault Circuit Interrupters) trip when an arc - across two conductors, or along one - is caused by damaged, overheated, or stressed electrical wiring or devices. Arc faults can occur when older wires become frayed or cracked, when a nail or screw damages a wire behind a wall, or when outlets or circuits are overburdened. It is that last item that is likely of interest with the automated controls, but if you use wire that is of the correct current-carrying capacity, and all connections are solid, that shouldn't be an issue.

My greenhouse in PA had a cutoff switch in my main panel in the basement of the house, which disconnected all electricity from the structure.

I ran 220 to the GH - 2 "hot" legs, one common, and one ground. In the greenhouse, I split that into two, 110V circuits - 1 hot+common+ground on each. I also added another ground stake just outside of the back of the structure to be safe. In other words, that 220V line ground was attached to both the house ground and the greenhouse ground.

What you need to do is look up the maximum current ratings of every device you want to operate in the greenhouse, making sure that the sum does not exceed the 60 amp service you currently have.
The smart thing to do would be to have a breaker in the subpanel for each device, and have each of them connected via a GFCI.
__________________
Ray Barkalow, Orchid Iconoclast
FIRSTRAYS.COM
Try Kelpak - you won't be sorry!
Reply With Quote
Post Thanks / Like - 1 Likes
Likes Rothrock42 liked this post
  #4  
Old 08-16-2022, 03:53 PM
Rothrock42 Rothrock42 is offline
Senior Member
 

Join Date: Dec 2015
Location: Portland, Oregon, USA
Posts: 283
Default

rbarata -- because it is less than 200 sq ft (18.5 sq m) the building itself didn't need to be permitted. Homeowners are allowed to do their own electrical work which I've done before -- just not in a damp location.

ray -- Yeah the sub panel has two grounding rods more than 6 feet apart at the building (and the main panel in the garage is also grounded. I'm using flexible non-metallic conduit, so I be running an actual grounding wire to each fixture and box.

There isn't enough space in the panel for each device to have its own breaker. The subpanel specification says it has 4 spaces and can support 8 circuits, but I haven't been able to locate half-height breakers that are compatible, so I assume I'll just be able to fit 4 at most.

The winter heat is natural gas, so there isn't a lot of electric demand

I have totaled it up and I'm a bit over 12 amps for everything I'm currently planning. If I go with 3 circuits for now -- air circulation, heat exhaust, and mist/water pumps -- that ends up 3 to 4.5 amps on a circuit and I think I should be fine and have some room to grow.

All the outlets I have are gfci and have the in-use all weather covers. I just wasn't sure if the gfci would have issues with the additional controls.
Reply With Quote
  #5  
Old 08-16-2022, 05:05 PM
Ray's Avatar
Ray Ray is offline
Senior Member
 

Join Date: May 2005
Member of:AOS
Location: Oak Island NC
Posts: 15,149
Electric system Male
Default

I went far more "laissez faire"....

My "electrical panel" was a water-tight electrical box, similar to the attached picture, but considerably larger and with three vertical terminal strips plus a fourth across the bottom for the ground.

The 220 came in through the back, with the two "hot" strips on either side of the central "common". My various GFCI outlets were mounted through the sides (silicone-sealed) and wired to the bus bars. No individual breakers.
Attached Images
File Type: jpg box.jpg (9.9 KB, 51 views)
__________________
Ray Barkalow, Orchid Iconoclast
FIRSTRAYS.COM
Try Kelpak - you won't be sorry!

Last edited by Ray; 08-16-2022 at 05:08 PM..
Reply With Quote
Post Thanks / Like - 1 Likes
Likes Rothrock42 liked this post
  #6  
Old 08-16-2022, 06:32 PM
Rothrock42 Rothrock42 is offline
Senior Member
 

Join Date: Dec 2015
Location: Portland, Oregon, USA
Posts: 283
Default

lol...yes that looks a bit more "laissez faire"!

Thanks for the thoughts. I think I'm going to get this done pretty soon. Awesome.
Reply With Quote
  #7  
Old 08-16-2022, 08:18 PM
Roberta's Avatar
Roberta Roberta is online now
Super Moderator
 

Join Date: Jun 2008
Zone: 10a
Location: Coastal southern California, USA
Posts: 13,738
Electric system Female
Default

I did have my GH wired by an electrician. One thing he did, very important, is somehow the GFCI on each outlet is independent of the others... so if one blows, it doesn't take the others down. (It's all once circuit, but each outlet can do its thing independently) I don't know how it was done (that's why I hired a professional), but clearly it is do-able. And it wasn't prohibitively expensive.... for someone who knows what they're doing it apparently is pretty easy. (In general, since I know very little about construction matters, I discuss with the professional what I want to accomplish, but let them figure out how to do it. I have gotten some very creative, functional solutions that way)
__________________
Orchids teach patience!

Roberta's Orchids (visit my back yard)

See what orchid species are blooming in Southern California(New page for NOVEMBER 2024)

Last edited by Roberta; 08-16-2022 at 08:24 PM..
Reply With Quote
Post Thanks / Like - 1 Likes
Likes Rothrock42 liked this post
Reply

Bookmarks

Tags
breaker, breakers, building, circuit, fans


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Charlie's misting system Keysguy Advanced Discussion 5 11-25-2020 12:32 PM
Safety of a Misting System in a Grow Tent? wperdrizet Growing Under Lights 4 10-19-2019 10:29 AM
New RO system smokinjoe1952 Beginner Discussion 8 04-11-2017 05:58 PM
Help me design a s/h watering system Rivka Semi-Hydroponic Culture 11 02-08-2012 05:50 PM
Mistking system arrived a few days early! YAY!!! cb977 Vendor Feedback 12 07-12-2010 06:02 PM

All times are GMT -4. The time now is 11:35 AM.

© 2007 OrchidBoard.com
Search Engine Optimisation provided by DragonByte SEO v2.0.37 (Lite) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.
Feedback Buttons provided by Advanced Post Thanks / Like (Lite) - vBulletin Mods & Addons Copyright © 2024 DragonByte Technologies Ltd.

Clubs vBulletin Plugins by Drive Thru Online, Inc.